Auto Insurance Life Insurance Health Insurance Family Insurance Travel Insurance Mortgage Insurance Accident Insurance Buying Insurance Housing Insurance Personal Insurance Medical Insurance Property Insurance Pregnant Insurance Internet Insurance Mobile Insurance Pet Insurance Employee Insurance Dental Insurance Liability Insurance Baby Insurance Children Insurance Boat Insurance Cancer Insurance Insurance Quotes Others
]

Calculating House Heat Loss From Utility Bills

Calculating House Heat Loss From Utility Bills

Here is a sample calculation, using a three-month meter reading for a typical house

. You can use any period (but at least two weeks of winter weather is necessary). You can read the meter yourself for the information, look at your furnace bills or phone your utility to see if they have appropriate records. The natural gas usage of other gas-fired appliances in the house is estimated from gas utility data and subtracted from the total for the period in question, so that the gas requirement for heating can be isolated. (Oil furnaces are harder to size using this method, but it may be possible using oil fill-up intervals and the number of litres delivered.)

The goal is to find a relationship between the gas consumed and the heating degree days (HDD). A heating degree day is essentially the number of degrees of heating required over the course of 24 hours, compared to a reference temperature of 18C. For example, if the average daily outside temperature is 10C, then the number of heating degree days for that day is 18C - 10C = 8 HDD. You can get the approximate HDD for your calculation period from the Environment Canada website. Use the data from the Degree Days: Below 18C row.

Once the relationship of the HDD and gas consumption is established, then you can calculate gas consumption for the design temperature in your area. This temperature is usually available from a mechanical contractor or your local building officials. It is not the extreme minimum temperature; it can be estimated from the average temperature over 24 hours on the coldest day of the winter. To approximate the design temperature: go to the historical weather data for your community on the Environment Canada website; find the coldest January over the last several years; then pick out the lowest daily average temperature in that month; and use that as the design temperature. Being a degree or two out will not make a huge difference in the calculation.

The example below uses a design temperature of -35C. At that temperature, the maximum HDD per day is equal to 53, which is the difference between 18C and -35C. Calculating the size of the furnace necessary on the coldest day of the year will mean that the furnace has the capacity to handle any expected local temperature. You can find a furnaces efficiency rating on its EnerGuide label or in the product documentation.Calculating House Heat Loss From Utility Bills


Example

Total gas consumption from December to March = 1,320 m3

Estimated consumption for other gas appliances (data from utility) = 306 m3

Therefore, gas consumption during the period for heating = 1,320 - 306 = 1,014 m3

Heating degree days for that period (from Environment Canada data) = 2,840 HDD

Heating consumption by degree day = 1,014 m3/ 2,840 HDD = 0.3570 m3/HDD

Heating consumption at 53 HDD/day = (53 HDD/day)(0.3570 m3/HDD) = 18.9 m3/day

Where gas has an energy content of 37.5 MJ/m3, and the existing furnace has an efficiency of 72 per cent, then:

Heat loss at 53 HDD/day = (18.9 m3/day) (37.5 MJ/m3)(0.72) = 510 MJ/day or 21.3 MJ/h*

According to the energy content of electricity, 3.6 MJ/h = 1 kW, then 21.3 MJ/h = 5.9 kW

This heat loss would require a furnace that produces an output of 5.9 kW or about 20,100 Btu/h (1 kW is approximately 3,412 Btu/h).Calculating House Heat Loss From Utility Bills


If we allow the CAN/CSA F280 permissible oversizing of 40 per cent, then the proper furnace sizing would be (1.4)(20,100 Btu/h) = approximately 28,100 Btu/h.

If you are calculating for an oil furnace, heating oil has an energy content of 38.2 MJ/litre.

* Note: This calculation is correct, although many people think the efficiency factor is in the wrong place. It is not. We are calculating the house heat loss based on fuel used and furnace efficiency. A more efficient furnace will have delivered more heat to the house, and the heat loss will be higher.

by: knock-knock
# 2 I recently tried cbda oil tincture as a replacement for the prime prematurely and was pleasantly surprised past the results. Initially skeptical, I found that it significantly helped with my appetite and doze issues without any remarkable side effects. The grease was unoppressive to speak, with legible dosage instructions. It had a indulgent, vulgar leaning that was not unpleasant. Within a week, I noticed a patent upgrading in my blanket well-being, feeling more blas‚ and rested. I appreciate the natural approach to wellness CBD offers and aim to pursue using it.   2024-2-20 05:50  reply
Buy Houses For Cash Humberside Why You Should Do That How You Can Avoid Spending More When Buying A House Property Management NYC Warehouse Management Systems – 5 Ways to Make Your Business More Efficient and More Profitable Serene Countryside Holidays At Sablet House Rental Provence by:Richard bacon Usual Considerations When House Hunting In Montpelier Real Estate Know About The Benefits Offered By Commercial Property Insurance We Buy Houses Providers Could Just Be The Ones You Need Renters Insurance Provides Coverage For Property Damage Insurance Policies for Your Business Property Hotel Liability And Property Insurance Determining The Best Large Dog House For A Canine Discover How To Keep Your House From Being On The Real Estate Market Too Long
Write post print
www.insurances.net guest:  register | login | search IP(18.224.95.38) Hovedstaden / Copenhagen Processed in 0.013253 second(s), 6 queries , Gzip enabled debug code: 36 , 3983, 966,
Copenhagen